Monitoring Basics ¶
This part of the Icinga 2 documentation provides an overview of all the basic monitoring concepts you need to know to run Icinga 2. Keep in mind these examples are made with a Linux server. If you are using Windows, you will need to change the services accordingly. See the ITL reference for further information.
Attribute Value Types ¶
The Icinga 2 configuration uses different value types for attributes.
| Type | Example |
| Number | 5 |
| Duration | 1m |
| String | "These are notes" |
| Boolean | true |
| Array | [ "value1", "value2" ] |
| Dictionary | { "key1" = "value1", "key2" = false } |
It is important to use the correct value type for object attributes as otherwise the configuration validation will fail.
Hosts and Services ¶
Icinga 2 can be used to monitor the availability of hosts and services. Hosts and services can be virtually anything which can be checked in some way:
- Network services (HTTP, SMTP, SNMP, SSH, etc.)
- Printers
- Switches or routers
- Temperature sensors
- Other local or network-accessible services
Host objects provide a mechanism to group services that are running on the same physical device.
Here is an example of a host object which defines two child services:
object Host "my-server1" {
address = "10.0.0.1"
check_command = "hostalive"
object Service "ping4" {
host_name = "my-server1"
check_command = "ping4"
object Service "http" {
check_command = "http"
The example creates two services ping4 and http which belong to the
host my-server1.
It also specifies that the host should perform its own check using the hostalive
check command.
The address attribute is used by check commands to determine which network
address is associated with the host object.
Details on troubleshooting check problems can be found here.
Host States ¶
Hosts can be in any one of the following states:
| Name | Description |
| UP | The host is available. |
| DOWN | The host is unavailable. |
Service States ¶
Services can be in any one of the following states:
| OK | The service is working properly. |
| WARNING | The service is experiencing some problems but is still considered to be in working condition. |
| CRITICAL | The check successfully determined that the service is in a critical state. |
| UNKNOWN | The check could not determine the service’s state. |
Check Result State Mapping ¶
Check plugins return
with an exit code which is converted into a state number.
Services map the states directly while hosts will treat 0 or 1 as UP
for example.
| Value | Host State | Service State |
| 0 | Up | OK |
| 1 | Up | Warning |
| 2 | Down | Critical |
| 3 | Down | Unknown |
Hard and Soft States ¶
When detecting a problem with a host/service, Icinga re-checks the object a number of
times (based on the max_check_attempts and retry_interval settings) before sending
notifications. This ensures that no unnecessary notifications are sent for
transient failures. During this time the object is in a SOFT state.
After all re-checks have been executed and the object is still in a non-OK
state, the host/service switches to a HARD state and notifications are sent.
| HARD | The host/service’s state hasn’t recently changed. check_interval applies here. |
| SOFT | The host/service has recently changed state and is being re-checked with retry_interval. |
Host and Service Checks ¶
Hosts and services determine their state by running checks in a regular interval.
object Host "router" {
The hostalive command is one of several built-in check commands. It sends ICMP
echo requests to the IP address specified in the address attribute to determine
whether a host is online.
Tip
hostaliveis the same aspingbut with different default thresholds. Both use thepingCLI command to execute sequential checks.If you need faster ICMP checks, look into the icmp CheckCommand.
A number of other built-in check commands are also available. In addition to these commands the next few chapters will explain in detail how to set up your own check commands.
Host Check Alternatives ¶
If the host is not reachable with ICMP, HTTP, etc. you can also use the dummy CheckCommand to set a default state.
object Host "dummy-host" {
check_command = "dummy"
vars.dummy_state = 0 //Up
vars.dummy_text = "Everything OK."
This method is also used when you send in external check results.
A more advanced technique is to calculate an overall state based on all services. This is described here.
Templates ¶
Templates may be used to apply a set of identical attributes to more than one object:
template Service "generic-service" {
max_check_attempts = 3
check_interval = 5m
retry_interval = 1m
enable_perfdata = true
apply Service "ping4" {
import "generic-service"
assign where host.address
apply Service "ping6" {
check_command = "ping6"
assign where host.address6
In this example the ping4 and ping6 services inherit properties from the
template generic-service.
Objects as well as templates themselves can import an arbitrary number of other templates. Attributes inherited from a template can be overridden in the object if necessary.
You can also import existing non-template objects.
Note
Templates and objects share the same namespace, i.e. you can’t define a template that has the same name like an object.
Multiple Templates ¶
The following example uses custom variables which
are provided in each template. The web-server template is used as the
base template for any host providing web services. In addition to that it
specifies the custom variable webserver_type, e.g. apache. Since this
template is also the base template, we import the generic-host template here.
This provides the check_command attribute by default and we don’t need
to set it anywhere later on.
template Host "web-server" {
import "generic-host"
vars = {
webserver_type = "apache"
The wp-server host template specifies a Wordpress instance and sets
the application_type custom variable. Please note the += operator
which adds dictionary items,
but does not override any previous vars attribute.
template Host "wp-server" {
vars += {
application_type = "wordpress"
The final host object imports both templates. The order is important here:
First the base template web-server is added to the object, then additional
attributes are imported from the wp-server object.
object Host "wp.example.com" {
import "web-server"
import "wp-server"
address = "192.168.56.200"
If you want to override specific attributes inherited from templates, you can specify them on the host object.
object Host "wp1.example.com" {
import "web-server"
import "wp-server"
vars.webserver_type = "nginx" //overrides attribute from base template
address = "192.168.56.201"
Custom Variables ¶
In addition to built-in object attributes you can define your own custom
attributes inside the vars attribute.
Tip
This is called
custom variablesthroughout the documentation, backends and web interfaces.Older documentation versions referred to this as
custom attribute.
The following example specifies the key ssh_port as custom
variable and assigns an integer value.
object Host "localhost" {
check_command = "ssh"
vars.ssh_port = 2222
vars is a dictionary where you
can set specific keys to values. The example above uses the shorter
indexer syntax.
An alternative representation can be written like this:
vars = {
ssh_port = 2222
or
vars["ssh_port"] = 2222
Custom Variable Values ¶
Valid values for custom variables include:
You can also define nested values such as dictionaries in dictionaries.
This example defines the custom variable disks as dictionary.
The first key is set to disk / is itself set to a dictionary
with one key-value pair.
vars.disks["disk /"] = {
disk_partitions = "/"
This can be written as resolved structure like this:
vars = {
disks = {
"disk /" = {
Keep this in mind when trying to access specific sub-keys in apply rules or functions.
Another example which is shown in the example configuration:
vars.notification["mail"] = {
groups = [ "icingaadmins" ]
This defines the notification custom variable as dictionary
with the key mail. Its value is a dictionary with the key groups
which itself has an array as value. Note: This array is the exact
same as the user_groups attribute for notification apply rules
expects.
vars.notification = {
mail = {
groups = [
"icingaadmins"
Functions as Custom Variables ¶
Icinga 2 lets you specify functions for custom variables. The special case here is that whenever Icinga 2 needs the value for such a custom variable it runs the function and uses whatever value the function returns:
object CheckCommand "random-value" {
command = [ PluginDir + "/check_dummy", "0", "$text$" ]
vars.text = {{ Math.random() * 100 }}
This example uses the abbreviated lambda syntax.
These functions have access to a number of variables:
| Variable | Description |
| user | The User object (for notifications). |
| service | The Service object (for service checks/notifications/event handlers). |
| host | The Host object. |
| command | The command object (e.g. a CheckCommand object for checks). |
Here’s an example:
vars.text = {{ host.check_interval }}
In addition to these variables the macro function can be used to retrieve the value of arbitrary macro expressions:
vars.text = {{
if (macro("$address$") == "127.0.0.1") {
log("Running a check for localhost!")
return "Some text"
The resolve_arguments function can be used to resolve a command and its arguments much in
the same fashion Icinga does this for the command and arguments attributes for
commands. The by_ssh command uses this functionality to let users specify a
command and arguments that should be executed via SSH:
arguments = {
"-C" = {{
var command = macro("$by_ssh_command$")
var arguments = macro("$by_ssh_arguments$")
if (typeof(command) == String && !arguments) {
return command
var escaped_args = []
for (arg in resolve_arguments(command, arguments)) {
escaped_args.add(escape_shell_arg(arg))
return escaped_args.join(" ")
Accessing object attributes at runtime inside these functions is described in the advanced topics chapter.
Runtime Macros ¶
Macros can be used to access other objects’ attributes and custom variables at runtime. For example they are used in command definitions to figure out which IP address a check should be run against:
object CheckCommand "my-ping" {
command = [ PluginDir + "/check_ping" ]
arguments = {
"-H" = "$ping_address$"
"-w" = "$ping_wrta$,$ping_wpl$%"
"-c" = "$ping_crta$,$ping_cpl$%"
"-p" = "$ping_packets$"
// Resolve from a host attribute, or custom variable.
vars.ping_address = "$address$"
// Default values
vars.ping_wrta = 100
vars.ping_wpl = 5
vars.ping_crta = 250
vars.ping_cpl = 10
vars.ping_packets = 5
check_command = "my-ping"
In this example we are using the $address$ macro to refer to the host’s address
attribute.
We can also directly refer to custom variables, e.g. by using $ping_wrta$. Icinga
automatically tries to find the closest match for the attribute you specified. The
exact rules for this are explained in the next section.
Note
When using the
$sign as single character you must escape it with an additional dollar character ($$).
Evaluation Order ¶
When executing commands Icinga 2 checks the following objects in this order to look up macros and their respective values:
- User object (only for notifications)
- Service object
- Host object
- Command object
- Global custom variables in the
Varsconstant
This execution order allows you to define default values for custom variables in your command objects.
Here’s how you can override the custom variable ping_packets from the previous
example:
object Service "ping" {
host_name = "localhost"
vars.ping_packets = 10 // Overrides the default value of 5 given in the command
If a custom variable isn’t defined anywhere, an empty value is used and a warning is written to the Icinga 2 log.
You can also directly refer to a specific attribute – thereby ignoring these evaluation rules – by specifying the full attribute name:
$service.vars.ping_wrta$
This retrieves the value of the ping_wrta custom variable for the service. This
returns an empty value if the service does not have such a custom variable no matter
whether another object such as the host has this attribute.
Host Runtime Macros ¶
The following host custom variables are available in all commands that are executed for hosts or services:
| host.name | The name of the host object. |
| host.display_name | The value of the display_name attribute. |
| host.state | The host’s current state. Can be one of UNREACHABLE, UP and DOWN. |
| host.state_id | The host’s current state. Can be one of 0 (up), 1 (down) and 2 (unreachable). |
| host.state_type | The host’s current state type. Can be one of SOFT and HARD. |
| host.check_attempt | The current check attempt number. |
| host.max_check_attempts | The maximum number of checks which are executed before changing to a hard state. |
| host.last_state | The host’s previous state. Can be one of UNREACHABLE, UP and DOWN. |
| host.last_state_id | The host’s previous state. Can be one of 0 (up), 1 (down) and 2 (unreachable). |
| host.last_state_type | The host’s previous state type. Can be one of SOFT and HARD. |
| host.last_state_change | The last state change’s timestamp. |
| host.downtime_depth | The number of active downtimes. |
| host.duration_sec | The time since the last state change. |
| host.latency | The host’s check latency. |
| host.execution_time | The host’s check execution time. |
| host.output | The last check’s output. |
| host.perfdata | The last check’s performance data. |
| host.last_check | The timestamp when the last check was executed. |
| host.check_source | The monitoring instance that performed the last check. |
| host.num_services | Number of services associated with the host. |
| host.num_services_ok | Number of services associated with the host which are in an OK state. |
| host.num_services_warning | Number of services associated with the host which are in a WARNING state. |
| host.num_services_unknown | Number of services associated with the host which are in an UNKNOWN state. |
| host.num_services_critical | Number of services associated with the host which are in a CRITICAL state. |
In addition to these specific runtime macros host object attributes can be accessed too.
Service Runtime Macros ¶
The following service macros are available in all commands that are executed for services:
| service.name | The short name of the service object. |
| service.display_name | The value of the display_name attribute. |
| service.check_command | The short name of the command along with any arguments to be used for the check. |
| service.state | The service’s current state. Can be one of OK, WARNING, CRITICAL and UNKNOWN. |
| service.state_id | The service’s current state. Can be one of 0 (ok), 1 (warning), 2 (critical) and 3 (unknown). |
| service.state_type | The service’s current state type. Can be one of SOFT and HARD. |
| service.check_attempt | The current check attempt number. |
| service.max_check_attempts | The maximum number of checks which are executed before changing to a hard state. |
| service.last_state | The service’s previous state. Can be one of OK, WARNING, CRITICAL and UNKNOWN. |
| service.last_state_id | The service’s previous state. Can be one of 0 (ok), 1 (warning), 2 (critical) and 3 (unknown). |
| service.last_state_type | The service’s previous state type. Can be one of SOFT and HARD. |
| service.last_state_change | The last state change’s timestamp. |
| service.downtime_depth | The number of active downtimes. |
| service.duration_sec | The time since the last state change. |
| service.latency | The service’s check latency. |
| service.execution_time | The service’s check execution time. |
| service.output | The last check’s output. |
| service.perfdata | The last check’s performance data. |
| service.last_check | The timestamp when the last check was executed. |
| service.check_source | The monitoring instance that performed the last check. |
In addition to these specific runtime macros service object attributes can be accessed too.
Command Runtime Macros ¶
The following custom variables are available in all commands:
| command.name | The name of the command object. |
User Runtime Macros ¶
The following custom variables are available in all commands that are executed for users:
| user.name | The name of the user object. |
| user.display_name | The value of the display_name attribute. |
In addition to these specific runtime macros user object attributes can be accessed too.
Notification Runtime Macros ¶
| notification.type | The type of the notification. |
| notification.author | The author of the notification comment if existing. |
| notification.comment | The comment of the notification if existing. |
In addition to these specific runtime macros notification object attributes can be accessed too.
Global Runtime Macros ¶
The following macros are available in all executed commands:
| icinga.timet | Current UNIX timestamp. |
| icinga.long_date_time | Current date and time including timezone information. Example: 2014-01-03 11:23:08 +0000 |
| icinga.short_date_time | Current date and time. Example: 2014-01-03 11:23:08 |
| icinga.date | Current date. Example: 2014-01-03 |
| icinga.time | Current time including timezone information. Example: 11:23:08 +0000 |
| icinga.uptime | Current uptime of the Icinga 2 process. |
The following macros provide global statistics:
| icinga.num_services_ok | Current number of services in state ‘OK’. |
| icinga.num_services_warning | Current number of services in state ‘Warning’. |
| icinga.num_services_critical | Current number of services in state ‘Critical’. |
| icinga.num_services_unknown | Current number of services in state ‘Unknown’. |
| icinga.num_services_pending | Current number of pending services. |
| icinga.num_services_unreachable | Current number of unreachable services. |
| icinga.num_services_flapping | Current number of flapping services. |
| icinga.num_services_in_downtime | Current number of services in downtime. |
| icinga.num_services_acknowledged | Current number of acknowledged service problems. |
| icinga.num_hosts_up | Current number of hosts in state ‘Up’. |
| icinga.num_hosts_down | Current number of hosts in state ‘Down’. |
| icinga.num_hosts_unreachable | Current number of unreachable hosts. |
| icinga.num_hosts_pending | Current number of pending hosts. |
| icinga.num_hosts_flapping | Current number of flapping hosts. |
| icinga.num_hosts_in_downtime | Current number of hosts in downtime. |
| icinga.num_hosts_acknowledged | Current number of acknowledged host problems. |
Apply Rules ¶
Several object types require an object relation, e.g. Service, Notification, Dependency, ScheduledDowntime objects. The object relations are documented in the linked chapters.
If you for example create a service object you have to specify the host_name attribute and reference an existing host attribute.
host_name = "icinga2-agent1.localdomain"
This isn’t comfortable when managing a huge set of configuration objects which could match on a common pattern.
Instead you want to use apply rules.
If you want basic monitoring for all your hosts, add a ping4 service apply rule
for all hosts which have the address attribute specified. Just one rule for 1000 hosts
instead of 1000 service objects. Apply rules will automatically generate them for you.
More explanations on assign where expressions can be found here.
Apply Rules: Prerequisites ¶
Before you start with apply rules keep the following in mind:
- Define the best match.
- A set of unique custom variables for these hosts/services?
- Or group memberships, e.g. a host being a member of a hostgroup which should have a service set?
- A generic pattern match on the host/service name?
- Multiple expressions combined with
&&or||operators
- All expressions must return a boolean value (an empty string is equal to
falsee.g.)
More specific object type requirements are described in these chapters:
- Apply services to hosts
- Apply notifications to hosts and services
- Apply dependencies to hosts and services
- Apply scheduled downtimes to hosts and services
Apply Rules: Usage Examples ¶
You can set/override object attributes in apply rules using the respectively available objects in that scope (host and/or service objects).
vars.application_type = host.vars.application_type
Custom variables can also store nested dictionaries and arrays. That way you can use them for not only matching for their existence or values in apply expressions, but also assign (“inherit”) their values into the generated objected from apply rules.
Remember the examples shown for custom variable values:
You can do two things here:
- Check for the existence of the
notificationcustom variable and its nested dictionary keymail. If this is boolean true, the notification object will be generated. - Assign the value of the
groupskey to theuser_groupsattribute.
apply Notification "mail-icingaadmin" to Host {
user_groups = host.vars.notification.mail.groups
assign where host.vars.notification.mail
A more advanced example is to use apply rules with for loops on arrays or dictionaries provided by custom atttributes or groups.
You can iterate over all dictionary keys defined in disks.
You can optionally use the value to specify additional object attributes.
vars.disk_partitions = config.disk_partitions
Please read the apply for chapter for more specific insights.
Tip
Building configuration in that dynamic way requires detailed information of the generated objects. Use the
object listCLI command after successful configuration validation.
Apply Rules Expressions ¶
You can use simple or advanced combinations of apply rule expressions. Each
expression must evaluate into the boolean true value. An empty string
will be for instance interpreted as false. In a similar fashion undefined
attributes will return false.
Returns false:
assign where host.vars.attribute_does_not_exist
Multiple assign where condition rows are evaluated as OR condition.
You can combine multiple expressions for matching only a subset of objects. In some cases,
you want to be able to add more than one assign/ignore where expression which matches
a specific condition. To achieve this you can use the logical and and or operators.
Apply Rules Expressions Examples ¶
Assign a service to a specific host in a host group array using the in operator:
assign where "hostgroup-dev" in host.groups
Assign an object when a custom variable is equal to a value:
assign where host.vars.application_type == "database"
assign where service.vars.sms_notify == true
Assign an object if a dictionary contains a given key:
assign where host.vars.app_dict.contains("app")
Match the host name by either using a case insensitive match:
assign where match("webserver*", host.name)
Match the host name by using a regular expression. Please note the escaped backslash character:
assign where regex("^webserver-[\\d+]", host.name)
Match all *mysql* patterns in the host name and (&&) custom variable prod_mysql_db
matches the db-* pattern. All hosts with the custom variable test_server set to true
should be ignored, or any host name ending with *internal pattern.
object HostGroup "mysql-server" {
display_name = "MySQL Server"
assign where match("*mysql*", host.name) && match("db-*", host.vars.prod_mysql_db)
ignore where host.vars.test_server == true
ignore where match("*internal", host.name)
Similar example for advanced notification apply rule filters: If the service
attribute notes matches the has gold support 24x7 string AND one of the
two condition passes, either the customer host custom variable is set to customer-xy
OR the host custom variable always_notify is set to true.
The notification is ignored for services whose host name ends with *internal
OR the priority custom variable is less than 2.
template Notification "cust-xy-notification" {
users = [ "noc-xy", "mgmt-xy" ]
command = "mail-service-notification"
apply Notification "notify-cust-xy-mysql" to Service {
import "cust-xy-notification"
assign where match("*has gold support 24x7*", service.notes) && (host.vars.customer == "customer-xy" || host.vars.always_notify == true)
ignore where match("*internal", host.name) || (service.vars.priority < 2 && host.vars.is_clustered == true)
More advanced examples are covered here.
Apply Services to Hosts ¶
The sample configuration already includes a detailed example in hosts.conf and services.conf for this use case.
The example for ssh applies a service object to all hosts with the address
attribute being defined and the custom variable os set to the string Linux in vars.
apply Service "ssh" {
assign where host.address && host.vars.os == "Linux"
Other detailed examples are used in their respective chapters, for example apply services with custom command arguments.
Apply Notifications to Hosts and Services ¶
Notifications are applied to specific targets (Host or Service) and work in a similar
manner:
apply Notification "mail-noc" to Service {
import "mail-service-notification"
user_groups = [ "noc" ]
In this example the mail-noc notification will be created as object for all services having the
notification.mail custom variable defined. The notification command is set to mail-service-notification
and all members of the user group noc will get notified.
It is also possible to generally apply a notification template and dynamically overwrite values from the template by checking for custom variables. This can be achieved by using conditional statements:
apply Notification "host-mail-noc" to Host {
import "mail-host-notification"
// replace interval inherited from `mail-host-notification` template with new notfication interval set by a host custom variable
if (host.vars.notification_interval) {
interval = host.vars.notification_interval
// same with notification period
if (host.vars.notification_period) {
period = host.vars.notification_period
// Send SMS instead of email if the host's custom variable `notification_type` is set to `sms`
if (host.vars.notification_type == "sms") {
command = "sms-host-notification"
} else {
command = "mail-host-notification"
In the example above the notification template mail-host-notification
contains all relevant notification settings.
The apply rule is applied on all host objects where the host.address is defined.
If the host object has a specific custom variable set, its value is inherited
into the local notification object scope, e.g. host.vars.notification_interval,
host.vars.notification_period and host.vars.notification_type.
This overwrites attributes already specified in the imported mail-host-notification
template.
The corresponding host object could look like this:
object Host "host1" {
import "host-linux-prod"
display_name = "host1"
address = "192.168.1.50"
vars.notification_interval = 1h
vars.notification_period = "24x7"
vars.notification_type = "sms"
Apply Dependencies to Hosts and Services ¶
Detailed examples can be found in the dependencies chapter.
Apply Recurring Downtimes to Hosts and Services ¶
The sample configuration includes an example in downtimes.conf.
Detailed examples can be found in the recurring downtimes chapter.
Using Apply For Rules ¶
Next to the standard way of using apply rules there is the requirement of applying objects based on a set (array or dictionary) using apply for expressions.
Take the following example: A host provides the snmp oids for different service check types. This could look like the following example:
object Host "router-v6" {
address6 = "2001:db8:1234::42"
vars.oids["if01"] = "1.1.1.1.1"
vars.oids["temp"] = "1.1.1.1.2"
vars.oids["bgp"] = "1.1.1.1.5"
The idea is to create service objects for if01 and temp but not bgp.
The oid value should also be used as service custom variable snmp_oid.
This is the command argument required by the snmp
check command.
The service’s display_name should be set to the identifier inside the dictionary,
e.g. if01.
apply Service for (identifier => oid in host.vars.oids) {
check_command = "snmp"
display_name = identifier
vars.snmp_oid = oid
ignore where identifier == "bgp" //don't generate service for bgp checks
Icinga 2 evaluates the apply for rule for all objects with the custom variable
oids set.
It iterates over all dictionary items inside the for loop and evaluates the
assign/ignore where expressions. You can access the loop variable
in these expressions, e.g. to ignore specific values.
In this example the bgp identifier is ignored. This avoids to generate
unwanted services. A different approach would be to match the oid value with a
regex/wildcard match pattern for example.
ignore where regex("^\d.\d.\d.\d.5$", oid)
Note
You don’t need an
assign whereexpression which checks for the existence of theoidscustom variable.
This method saves you from creating multiple apply rules. It also moves the attribute specification logic from the service to the host.
Apply For and Custom Variable Override ¶
Imagine a different more advanced example: You are monitoring your network device (host) with many interfaces (services). The following requirements/problems apply:
- Each interface service should be named with a prefix and a name defined in your host object (which could be generated from your CMDB, etc.)
- Each interface has its own VLAN tag
- Some interfaces have QoS enabled
- Additional attributes such as
display_nameornotes,notes_urlandaction_urlmust be dynamically generated.
Tip
Define the SNMP community as global constant in your constants.conf file.
const IftrafficSnmpCommunity = "public"
Define the interfaces custom variable
on the cisco-catalyst-6509-34 host object and add three example interfaces as dictionary keys.
Specify additional attributes inside the nested dictionary as learned with custom variable values:
object Host "cisco-catalyst-6509-34" {
display_name = "Catalyst 6509 #34 VIE21"
address = "127.0.1.4"
/* "GigabitEthernet0/2" is the interface name,
* and key name in service apply for later on
vars.interfaces["GigabitEthernet0/2"] = {
/* define all custom variables with the
* same name required for command parameters/arguments
* in service apply (look into your CheckCommand definition)
iftraffic_units = "g"
iftraffic_community = IftrafficSnmpCommunity
iftraffic_bandwidth = 1
vlan = "internal"
qos = "disabled"
vars.interfaces["GigabitEthernet0/4"] = {
//iftraffic_community = IftrafficSnmpCommunity
vlan = "remote"
qos = "enabled"
vars.interfaces["MgmtInterface1"] = {
vlan = "mgmt"
interface_address = "127.99.0.100" #special management ip
Start with the apply for definition and iterate over host.vars.interfaces.
This is a dictionary and should use the variables interface_name as key
and interface_config as value for each generated object scope.
"if-" specifies the object name prefix for each service which results
in if-<interface_name> for each iteration.
/* loop over the host.vars.interfaces dictionary
* for (key => value in dict) means `interface_name` as key
* and `interface_config` as value. Access config attributes
* with the indexer (`.`) character.
apply Service "if-" for (interface_name => interface_config in host.vars.interfaces) {
Import the generic-service template, assign the iftraffic
check_command. Use the dictionary key interface_name to set a proper display_name
string for external interfaces.
check_command = "iftraffic"
display_name = "IF-" + interface_name
The interface_name key’s value is the same string used as command parameter for
iftraffic:
/* use the key as command argument (no duplication of values in host.vars.interfaces) */
vars.iftraffic_interface = interface_name
Remember that interface_config is a nested dictionary. In the first iteration it looks
like this:
interface_config = {
vlan = "internal"
qos = "disabled"
Access the dictionary keys with the indexer syntax
and assign them to custom variables used as command parameters for the iftraffic
check command.
/* map the custom variables as command arguments */
vars.iftraffic_units = interface_config.iftraffic_units
vars.iftraffic_community = interface_config.iftraffic_community
If you just want to inherit all attributes specified inside the interface_config
dictionary, add it to the generated service custom variables like this:
/* the above can be achieved in a shorter fashion if the names inside host.vars.interfaces
* are the _exact_ same as required as command parameter by the check command
* definition.
vars += interface_config
If the user did not specify default values for required service custom variables, add them here. This also helps to avoid unwanted configuration validation errors or runtime failures. Please read more about conditional statements here.
/* set a default value for units and bandwidth */
if (interface_config.iftraffic_units == "") {
vars.iftraffic_units = "m"
if (interface_config.iftraffic_bandwidth == "") {
vars.iftraffic_bandwidth = 1
if (interface_config.vlan == "") {
vars.vlan = "not set"
if (interface_config.qos == "") {
vars.qos = "not set"
If the host object did not specify a custom SNMP community,
set a default value specified by the global constant IftrafficSnmpCommunity.
/* set the global constant if not explicitely
* not provided by the `interfaces` dictionary on the host
if (len(interface_config.iftraffic_community) == 0 || len(vars.iftraffic_community) == 0) {
vars.iftraffic_community = IftrafficSnmpCommunity
Use the provided values to calculate more object attributes which can be e.g. seen in external interfaces.
/* Calculate some additional object attributes after populating the `vars` dictionary */
notes = "Interface check for " + interface_name + " (units: '" + interface_config.iftraffic_units + "') in VLAN '" + vars.vlan + "' with ' QoS '" + vars.qos + "'"
notes_url = "https://foreman.company.com/hosts/" + host.name
action_url = "https://snmp.checker.company.com/" + host.name + "/if-" + interface_name
Tip
Verify that the apply-for-rule successfully created the service objects with the inherited custom variables:
# icinga2 daemon -C
# icinga2 object list --type Service --name *catalyst*
Object 'cisco-catalyst-6509-34!if-GigabitEthernet0/2' of type 'Service':
* vars
% = modified in '/etc/icinga2/conf.d/iftraffic.conf', lines 59:3-59:26
* iftraffic_bandwidth = 1
* iftraffic_community = "public"
% = modified in '/etc/icinga2/conf.d/iftraffic.conf', lines 53:3-53:65
* iftraffic_interface = "GigabitEthernet0/2"
% = modified in '/etc/icinga2/conf.d/iftraffic.conf', lines 49:3-49:43
* iftraffic_units = "g"
% = modified in '/etc/icinga2/conf.d/iftraffic.conf', lines 52:3-52:57
* qos = "disabled"
* vlan = "internal"
Object 'cisco-catalyst-6509-34!if-GigabitEthernet0/4' of type 'Service':
* vars
% = modified in '/etc/icinga2/conf.d/iftraffic.conf', lines 79:5-79:53
* iftraffic_interface = "GigabitEthernet0/4"
* qos = "enabled"
* vlan = "remote"
Object 'cisco-catalyst-6509-34!if-MgmtInterface1' of type 'Service':
* vars
% = modified in '/etc/icinga2/conf.d/iftraffic.conf', lines 66:5-66:32
* iftraffic_interface = "MgmtInterface1"
* iftraffic_units = "m"
% = modified in '/etc/icinga2/conf.d/iftraffic.conf', lines 63:5-63:30
* interface_address = "127.99.0.100"
* qos = "not set"
% = modified in '/etc/icinga2/conf.d/iftraffic.conf', lines 72:5-72:24
* vlan = "mgmt"
Use Object Attributes in Apply Rules ¶
Since apply rules are evaluated after the generic objects, you can reference existing host and/or service object attributes as values for any object attribute specified in that apply rule.
object Host "opennebula-host" {
address = "10.1.1.2"
vars.hosting["cust1"] = {
http_uri = "/shop"
customer_name = "Customer 1"
customer_id = "7568"
support_contract = "gold"
vars.hosting["cust2"] = {
http_uri = "/"
customer_name = "Customer 2"
customer_id = "7569"
support_contract = "silver"
hosting is a custom variable with the Dictionary value type.
This is mandatory to iterate with the key => value notation
in the below apply for rule.
apply Service for (customer => config in host.vars.hosting) {
vars.qos = "disabled"
vars += config
vars.http_uri = "/" + customer + "/" + config.http_uri
display_name = "Shop Check for " + vars.customer_name + "-" + vars.customer_id
notes = "Support contract: " + vars.support_contract + " for Customer " + vars.customer_name + " (" + vars.customer_id + ")."
action_url = "https://snmp.checker.company.com/" + host.name + "/" + vars.customer_id
Each loop iteration has different values for customer and config`
in the local scope.
1.
customer = "cust 1"
config = {
http_uri = "/shop"
2.
customer = "cust2"
config = {
http_uri = "/"
You can now add the config dictionary into vars.
vars += config
Now it looks like the following in the first iteration:
customer = "cust 1"
vars = {
http_uri = "/shop"
Remember, you know this structure already. Custom attributes can also be accessed by using the indexer syntax.
vars.http_uri = ... + config.http_uri
can also be written as
vars += config
vars.http_uri = ... + vars.http_uri
Groups ¶
A group is a collection of similar objects. Groups are primarily used as a visualization aid in web interfaces.
Group membership is defined at the respective object itself. If
you have a hostgroup name windows for example, and want to assign
specific hosts to this group for later viewing the group on your
alert dashboard, first create a HostGroup object:
object HostGroup "windows" {
display_name = "Windows Servers"
Then add your hosts to this group:
template Host "windows-server" {
groups += [ "windows" ]
object Host "mssql-srv1" {
import "windows-server"
vars.mssql_port = 1433
object Host "mssql-srv2" {
This can be done for service and user groups the same way:
object UserGroup "windows-mssql-admins" {
display_name = "Windows MSSQL Admins"
template User "generic-windows-mssql-users" {
groups += [ "windows-mssql-admins" ]
object User "win-mssql-noc" {
import "generic-windows-mssql-users"
email = "noc@example.com"
object User "win-mssql-ops" {
email = "ops@example.com"
Group Membership Assign ¶
Instead of manually assigning each object to a group you can also assign objects to a group based on their attributes:
object HostGroup "prod-mssql" {
display_name = "Production MSSQL Servers"
assign where host.vars.mssql_port && host.vars.prod_mysql_db
In this example all hosts with the vars attribute mssql_port
will be added as members to the host group mssql. However, all
hosts matching the string \*internal
or with the test_server attribute set to true are not added to this group.
Details on the assign where syntax can be found in the
Language Reference.
Notifications ¶
Notifications for service and host problems are an integral part of your monitoring setup.
When a host or service is in a downtime, a problem has been acknowledged or the dependency logic determined that the host/service is unreachable, no notifications are sent. You can configure additional type and state filters refining the notifications being actually sent.
There are many ways of sending notifications, e.g. by email, XMPP, IRC, Twitter, etc. On its own Icinga 2 does not know how to send notifications. Instead it relies on external mechanisms such as shell scripts to notify users. More notification methods are listed in the addons and plugins chapter.
A notification specification requires one or more users (and/or user groups)
who will be notified in case of problems. These users must have all custom
attributes defined which will be used in the NotificationCommand on execution.
The user icingaadmin in the example below will get notified only on Warning and
Critical problems. In addition to that Recovery notifications are sent (they require
the OK state).
object User "icingaadmin" {
display_name = "Icinga 2 Admin"
enable_notifications = true
states = [ OK, Warning, Critical ]
types = [ Problem, Recovery ]
email = "icinga@localhost"
If you don’t set the states and types configuration attributes for the User
object, notifications for all states and types will be sent.
Details on troubleshooting notification problems can be found here.
Note
Make sure that the notification feature is enabled in order to execute notification commands.
You should choose which information you (and your notified users) are interested in case of emergency, and also which information does not provide any value to you and your environment.
An example notification command is explained here.
You can add all shared attributes to a Notification template which is inherited
to the defined notifications. That way you’ll save duplicated attributes in each
Notification object. Attributes can be overridden locally.
template Notification "generic-notification" {
interval = 15m
states = [ Warning, Critical, Unknown ]
types = [ Problem, Acknowledgement, Recovery, Custom, FlappingStart,
FlappingEnd, DowntimeStart, DowntimeEnd, DowntimeRemoved ]
period = "24x7"
The time period 24x7 is included as example configuration with Icinga 2.
Use the apply keyword to create Notification objects for your services:
import "generic-notification"
Instead of assigning users to notifications, you can also add the user_groups
attribute with a list of user groups to the Notification object. Icinga 2 will
send notifications to all group members.
Note
Only users who have been notified of a problem before (
Warning,Critical,Unknownstates for services,Downfor hosts) will receiveRecoverynotifications.
Icinga 2 v2.10 allows you to configure a User object with Acknowledgement and/or Recovery
without a Problem notification. These notifications will be sent without
any problem notifications beforehand, and can be used for e.g. ticket systems.
object User "ticketadmin" {
display_name = "Ticket Admin"
types = [ Acknowledgement, Recovery ]
email = "ticket@localhost"
Notifications: Users from Host/Service ¶
A common pattern is to store the users and user groups on the host or service objects instead of the notification object itself.
The sample configuration provided in hosts.conf and notifications.conf already provides an example for this question.
Tip
Please make sure to read the apply and custom variable values chapter to fully understand these examples.
Specify the user and groups as nested custom variable on the host object:
object Host "icinga2-agent1.localdomain" {
users = [ "icingaadmin" ]
vars.notification["sms"] = {
As you can see, there is the option to use two different notification
apply rules here: One for mail and one for sms.
This example assigns the users and groups nested keys from the notification
custom variable to the actual notification object attributes.
Since errors are hard to debug if host objects don’t specify the required configuration attributes, you can add a safety condition which logs which host object is affected.
critical/config: Host 'icinga2-client3.localdomain' does not specify required user/user_groups configuration attributes for notification 'mail-icingaadmin'.
You can also use the script debugger for more advanced insights.
apply Notification "mail-host-notification" to Host {
/* Log which host does not specify required user/user_groups attributes. This will fail immediately during config validation and help a lot. */
if (len(host.vars.notification.mail.users) == 0 && len(host.vars.notification.mail.user_groups) == 0) {
log(LogCritical, "config", "Host '" + host.name + "' does not specify required user/user_groups configuration attributes for notification '" + name + "'.")
users = host.vars.notification.mail.users
assign where host.vars.notification.mail && typeof(host.vars.notification.mail) == Dictionary
apply Notification "sms-host-notification" to Host {
if (len(host.vars.notification.sms.users) == 0 && len(host.vars.notification.sms.user_groups) == 0) {
users = host.vars.notification.sms.users
user_groups = host.vars.notification.sms.groups
assign where host.vars.notification.sms && typeof(host.vars.notification.sms) == Dictionary
The example above uses typeof as safety function to ensure that
the mail key really provides a dictionary as value. Otherwise
the configuration validation could fail if an admin adds something
like this on another host:
vars.notification.mail = "yes"
You can also do a more fine granular assignment on the service object:
apply Service "http" {
This notification apply rule is different to the one above. The service notification users and groups are inherited from the service and if not set, from the host object. A default user is set too.
apply Notification "mail-service-notification" to Service {
if (service.vars.notification.mail.users) {
users = service.vars.notification.mail.users
} else if (host.vars.notification.mail.users) {
} else {
/* Default user who receives everything. */
if (service.vars.notification.mail.groups) {
user_groups = service.vars.notification.mail.groups
} else if (host.vars.notification.mail.groups) {
assign where ( host.vars.notification.mail && typeof(host.vars.notification.mail) == Dictionary ) || ( service.vars.notification.mail && typeof(service.vars.notification.mail) == Dictionary )
Notification Escalations ¶
When a problem notification is sent and a problem still exists at the time of re-notification you may want to escalate the problem to the next support level. A different approach is to configure the default notification by email, and escalate the problem via SMS if not already solved.
You can define notification start and end times as additional configuration
attributes making the Notification object a so-called notification escalation.
Using templates you can share the basic notification attributes such as users or the
interval (and override them for the escalation then).
Using the example from above, you can define additional users being escalated for SMS notifications between start and end time.
object User "icinga-oncall-2nd-level" {
display_name = "Icinga 2nd Level"
vars.mobile = "+1 555 424642"
object User "icinga-oncall-1st-level" {
display_name = "Icinga 1st Level"
Define an additional NotificationCommand for SMS notifications.
Note
The example is not complete as there are many different SMS providers. Please note that sending SMS notifications will require an SMS provider or local hardware with an active SIM card.
object NotificationCommand "sms-notification" {
command = [
PluginDir + "/send_sms_notification",
"$mobile$",
The two new notification escalations are added onto the local host
and its service ping4 using the generic-notification template.
The user icinga-oncall-2nd-level will get notified by SMS (sms-notification
command) after 30m until 1h.
Note
The
intervalwas set to 15m in thegeneric-notificationtemplate example. Lower that value in your escalations by using a secondary template or by overriding the attribute directly in thenotificationsarray position forescalation-sms-2nd-level.
If the problem does not get resolved nor acknowledged preventing further notifications,
the escalation-sms-1st-level user will be escalated 1h after the initial problem was
notified, but only for one hour (2h as end key for the times dictionary).
apply Notification "mail" to Service {
command = "mail-notification"
assign where service.name == "ping4"
apply Notification "escalation-sms-2nd-level" to Service {
command = "sms-notification"
users = [ "icinga-oncall-2nd-level" ]
times = {
begin = 30m
end = 1h
apply Notification "escalation-sms-1st-level" to Service {
users = [ "icinga-oncall-1st-level" ]
times = {
begin = 1h
end = 2h
Notification Delay ¶
Sometimes the problem in question should not be announced when the notification is due
(the object reaching the HARD state), but after a certain period. In Icinga 2
you can use the times dictionary and set begin = 15m as key and value if you want to
postpone the notification window for 15 minutes. Leave out the end key – if not set,
Icinga 2 will not check against any end time for this notification.
Note
Setting the
endkey to0will stop sending notifications immediately when a problem occurs, effectively disabling the notification.
Make sure to specify a relatively low notification interval to get notified soon enough again.
interval = 5m
times.begin = 15m // delay notification window
Also note that this mechanism doesn’t take downtimes etc. into account, only
the HARD state change time matters. E.g. for a problem which occurred in the
middle of a downtime from 2 PM to 4 PM times.begin = 2h means 5 PM, not 6 PM.
Disable Re-notifications ¶
If you prefer to be notified only once, you can disable re-notifications by setting the
interval attribute to 0.
apply Notification "notify-once" to Service {
interval = 0 // disable re-notification
Notification Filters by State and Type ¶
If there are no notification state and type filter attributes defined at the Notification
or User object, Icinga 2 assumes that all states and types are being notified.
Available state and type filters for notifications are:
states = [ OK, Warning, Critical, Unknown ]
Commands ¶
Icinga 2 uses three different command object types to specify how checks should be performed, notifications should be sent, and events should be handled.
Check Commands ¶
CheckCommand objects define the command line how a check is called.
CheckCommand objects are referenced by
Host and Service objects
using the check_command attribute.
Note
Make sure that the checker feature is enabled in order to execute checks.
Integrate the Plugin with a CheckCommand Definition ¶
Unless you have done so already, download your check plugin and put it
into the PluginDir directory. The following example uses the
check_mysql plugin contained in the Monitoring Plugins package.
The plugin path and all command arguments are made a list of double-quoted string arguments for proper shell escaping.
Call the check_disk plugin with the --help parameter to see
all available options. Our example defines warning (-w) and
critical (-c) thresholds for the disk usage. Without any
partition defined (-p) it will check all local partitions.
icinga@icinga2 $ /usr/lib64/nagios/plugins/check_mysql --help
This program tests connections to a MySQL server
Usage:
check_mysql [-d database] [-H host] [-P port] [-s socket]
[-u user] [-p password] [-S] [-l] [-a cert] [-k key]
[-C ca-cert] [-D ca-dir] [-L ciphers] [-f optfile] [-g group]
Next step is to understand how command parameters are being passed from a host or service object, and add a CheckCommand definition based on these required parameters and/or default values.
Please continue reading in the plugins section for additional integration examples.
Passing Check Command Parameters from Host or Service ¶
Check command parameters are defined as custom variables which can be accessed as runtime macros by the executed check command.
The check command parameters for ITL provided plugin check command definitions are documented here, for example disk.
In order to practice passing command parameters you should integrate your own plugin.
The following example will use check_mysql provided by the Monitoring Plugins.
Define the default check command custom variables, for example mysql_user and mysql_password
(freely definable naming schema) and optional their default threshold values. You can
then use these custom variables as runtime macros for command arguments
on the command line.
Tip
Use a common command type as prefix for your command arguments to increase readability.
mysql_userhelps understanding the context better than justuseras argument.
The default custom variables can be overridden by the custom variables
defined in the host or service using the check command my-mysql. The custom variables
can also be inherited from a parent template using additive inheritance (+=).
# vim /etc/icinga2/conf.d/commands.conf
object CheckCommand "my-mysql" {
command = [ PluginDir + "/check_mysql" ] //constants.conf -> const PluginDir
arguments = {
"-H" = "$mysql_host$"
"-u" = {
required = true
value = "$mysql_user$"
"-p" = "$mysql_password$"
"-P" = "$mysql_port$"
"-s" = "$mysql_socket$"
"-a" = "$mysql_cert$"
"-d" = "$mysql_database$"
"-k" = "$mysql_key$"
"-C" = "$mysql_ca_cert$"
"-D" = "$mysql_ca_dir$"
"-L" = "$mysql_ciphers$"
"-f" = "$mysql_optfile$"
"-g" = "$mysql_group$"
"-S" = {
set_if = "$mysql_check_slave$"
description = "Check if the slave thread is running properly."
"-l" = {
set_if = "$mysql_ssl$"
description = "Use ssl encryption"
vars.mysql_check_slave = false
vars.mysql_ssl = false
vars.mysql_host = "$address$"
The check command definition also sets mysql_host to the $address$ default value. You can override
this command parameter if for example your MySQL host is not running on the same server’s ip address.
Make sure pass all required command parameters, such as mysql_user, mysql_password and mysql_database.
MysqlUsername and MysqlPassword are specified as global constants
in this example.
# vim /etc/icinga2/conf.d/services.conf
apply Service "mysql-icinga-db-health" {
check_command = "my-mysql"
vars.mysql_user = MysqlUsername
vars.mysql_password = MysqlPassword
vars.mysql_database = "icinga"
vars.mysql_host = "192.168.33.11"
assign where match("icinga2*", host.name)
ignore where host.vars.no_health_check == true
Take a different example: The example host configuration in hosts.conf
also applies an ssh service check. Your host’s ssh port is not the default 22, but set to 2022.
You can pass the command parameter as custom variable ssh_port directly inside the service apply rule
inside services.conf:
vars.ssh_port = 2022 //custom command parameter
assign where (host.address || host.address6) && host.vars.os == "Linux"
If you prefer this being configured at the host instead of the service, modify the host configuration object instead. The runtime macro resolving order is described here.
object Host "icinga2-agent1.localdomain {
Passing Check Command Parameters Using Apply For ¶
The host localhost with the generated services from the basic-partitions dictionary (see
apply for for details) checks a basic set of disk partitions
with modified custom variables (warning thresholds at 10%, critical thresholds at 5%
free disk space).
The custom variable disk_partition can either hold a single string or an array of
string values for passing multiple partitions to the check_disk check plugin.
object Host "my-server" {
address = "127.0.0.1"
address6 = "::1"
vars.local_disks["basic-partitions"] = {
disk_partitions = [ "/", "/tmp", "/var", "/home" ]
apply Service for (disk => config in host.vars.local_disks) {
check_command = "my-disk"
vars += config
vars.disk_wfree = "10%"
vars.disk_cfree = "5%"
More details on using arrays in custom variables can be found in this chapter.
Command Arguments ¶
Next to the short command array specified in the command object,
it is advised to define plugin/script parameters in the arguments
dictionary attribute.
The value of the --parameter key itself is a dictionary with additional
keys. They allow to create generic command objects and are also for documentation
purposes, e.g. with the description field copying the plugin’s help text in there.
The Icinga Director uses this field to show the argument’s purpose when selecting it.
arguments = {
"--parameter" = {
description = "..."
value = "..."
Each argument is optional by default and is omitted if the value is not set.
Learn more about integrating plugins with CheckCommand objects in this chapter.
There are additional possibilities for creating a command only once, with different parameters and arguments, shown below.
Command Arguments: Value ¶
In order to find out about the command argument, call the plugin’s help or consult the README.
./check_systemd.py --help
-u UNIT, --unit UNIT Name of the systemd unit that is beeing tested.
Whenever the long parameter name is available, prefer this over the short one.
arguments = {
"--unit" = {
Define a unique prefix for the command’s specific arguments. Best practice is to follow this schema:
<command name>_<parameter name>
Therefore use systemd_ as prefix, and use the long plugin parameter name unit inside the runtime macro
syntax.
arguments = {
"--unit" = {
value = "$systemd_unit$"
In order to specify a default value, specify a custom variable inside the CheckCommand object.
vars.systemd_unit = "icinga2"
This value can be overridden from the host/service object as command parameters.
Command Arguments: Description ¶
Best practice, also inside the ITL, is to always
copy the command parameter help output into the description
field of your check command.
With the example above, inspect the parameter’s help text.
Copy this into the command arguments description entry.
arguments = {
"--unit" = {
description = "Name of the systemd unit that is beeing tested."
Command Arguments: Required ¶
Specifies whether this command argument is required, or not. By default all arguments are optional.
Tip
Good plugins provide optional parameters in square brackets, e.g.
[-w SECONDS].
The required field can be toggled with a boolean value.
arguments = {
"--host" = {
value = "..."
description = "..."
required = true
Whenever the check is executed and the argument is missing, Icinga logs an error. This allows to better debug configuration errors instead of sometimes unreadable plugin errors when parameters are missing.
Command Arguments: Skip Key ¶
The arguments attribute requires a key, empty values are not allowed.
To overcome this for parameters which don’t need the name in front of
the value, use the skip_key boolean toggle.
command = [ PrefixDir + "/bin/icingacli", "businessprocess", "process", "check" ]
arguments = {
"--process" = {
value = "$icingacli_businessprocess_process$"
description = "Business process to monitor"
skip_key = true
required = true
order = -1
The service specifies the custom variable icingacli_businessprocess_process.
vars.icingacli_businessprocess_process = "bp-shop-web"
This results in this command line without the --process parameter:
'/bin/icingacli' 'businessprocess' 'process' 'check' 'bp-shop-web'
You can use this method to put everything into the arguments attribute
in a defined order and without keys. This avoids entries in the command
attributes too.
Command Arguments: Set If ¶
This can be used for the following scenarios:
Parameters without value, e.g. --sni.
command = [ PluginDir + "/check_http"]
arguments = {
"--sni" = {
set_if = "$http_sni$"
Whenever a host/service object sets the http_sni custom variable
to true, the parameter is added to the command line.
'/usr/lib64/nagios/plugins/check_http' '--sni'
Numeric values are allowed too.
Parameters with value, but additionally controlled with an extra custom variable boolean flag.
The following example is taken from the postgres CheckCommand. The host
parameter should use a value but only whenever the postgres_unixsocket
custom variable is set to false.
Note: set_if is using a runtime lambda function because the value
is evaluated at runtime. This is explained in this chapter.
command = [ PluginContribDir + "/check_postgres.pl" ]
arguments = {
"-H" = {
value = "$postgres_host$"
set_if = {{ macro("$postgres_unixsocket$") == false }}
description = "hostname(s) to connect to; defaults to none (Unix socket)"
An executed check for this host and services …
object Host "postgresql-cluster" {
vars.postgres_host = "192.168.56.200"
vars.postgres_unixsocket = false
… use the following command line:
'/usr/lib64/nagios/plugins/check_postgres.pl' '-H' '192.168.56.200'
Host/service objects which set postgres_unixsocket to false don’t add the -H parameter
and its value to the command line.
References: abbreviated lambda syntax, macro.
Command Arguments: Order ¶
Plugin may require parameters in a special order. One after the other, or e.g. one parameter always in the first position.
arguments = {
"--first" = {
value = "..."
description = "..."
order = -5
"--second" = {
value = "..."
description = "..."
order = -4
"--last" = {
value = "..."
description = "..."
order = 99
Keep in mind that positional arguments need to be tested thoroughly.
Command Arguments: Repeat Key ¶
Parameters can use Array as value type. Whenever Icinga encounters an array, it repeats the parameter key and each value element by default.
command = [ NscpPath + "\\nscp.exe", "client" ]
arguments = {
"-a" = {
value = "$nscp_arguments$"
description = "..."
repeat_key = true
On a host/service object, specify the nscp_arguments custom variable
as an array.
vars.nscp_arguments = [ "exclude=sppsvc", "exclude=ShellHWDetection" ]
This translates into the following command line:
nscp.exe 'client' '-a' 'exclude=sppsvc' '-a' 'exclude=ShellHWDetection'
If the plugin requires you to pass the list without repeating the key,
set repeat_key = false in the argument definition.
arguments = {
"-a" = {
description = "..."
repeat_key = false
nscp.exe 'client' '-a' 'exclude=sppsvc' 'exclude=ShellHWDetection'
Command Arguments: Key ¶
The arguments attribute requires unique keys. Sometimes, you’ll
need to override this in the resulting command line with same key
names. Therefore you can specifically override the arguments key.
arguments = {
"--key1" = {
value = "..."
key = "-specialkey"
"--key2" = {
value = "..."
key = "-specialkey"
This results in the following command line:
'-specialkey' '...' '-specialkey' '...'
Environment Variables ¶
The env command object attribute specifies a list of environment variables with values calculated
from custom variables which should be exported as environment variables prior to executing the command.
This is useful for example for hiding sensitive information on the command line output when passing credentials to database checks:
object CheckCommand "mysql" {
arguments = {
"-H" = "$mysql_address$"
vars.mysql_address = "$address$"
vars.mysql_user = "icinga_check"
vars.mysql_pass = "password"
env.MYSQLUSER = "$mysql_user$"
env.MYSQLPASS = "$mysql_pass$"
The executed command line visible with ps or top looks like this and hides
the database credentials in the user’s environment.
/usr/lib/nagios/plugins/check_mysql -H 192.168.56.101 -d icinga
Note
If the CheckCommand also supports setting the parameter in the command line, ensure to use a different name for the custom variable. Otherwise Icinga 2 adds the command line parameter.
If a specific CheckCommand object provided with the Icinga Template Library
needs additional environment variables, you can import it into a new custom
CheckCommand object and add additional env keys. Example for the mysql_health
CheckCommand:
object CheckCommand "mysql_health_env" {
import "mysql_health"
// https://labs.consol.de/nagios/check_mysql_health/
env.NAGIOS__SERVICEMYSQL_USER = "$mysql_health_env_username$"
env.NAGIOS__SERVICEMYSQL_PASS = "$mysql_health_env_password$"
Specify the custom variables mysql_health_env_username and mysql_health_env_password
in the service object then.
Note
Keep in mind that the values are still visible with the debug console and the inspect mode in the Icinga Director.
You can also set global environment variables in the application’s
sysconfig configuration file, e.g. HOME or specific library paths
for Oracle. Beware that these environment variables can be used
by any CheckCommand object and executed plugin and can leak sensitive
information.
Notification Commands ¶
NotificationCommand
objects define how notifications are delivered to external interfaces
(email, XMPP, IRC, Twitter, etc.).
NotificationCommand
objects are referenced by Notification
objects using the command attribute.
Note
While it’s possible to specify an entire notification command right
in the NotificationCommand object it is generally advisable to create a
shell script in the /etc/icinga2/scripts directory and have the
NotificationCommand object refer to that.
A fresh Icinga 2 install comes with with two example scripts for host
and service notifications by email. Based on the Icinga 2 runtime macros
(such as $service.output$ for the current check output) it’s possible
to send email to the user(s) associated with the notification itself
($user.email$). Feel free to take these scripts as a starting point
for your own individual notification solution - and keep in mind that
nearly everything is technically possible.
Information needed to generate notifications is passed to the scripts as
arguments. The NotificationCommand objects mail-host-notification and
mail-service-notification correspond to the shell scripts
mail-host-notification.sh and mail-service-notification.sh in
/etc/icinga2/scripts and define default values for arguments. These
defaults can always be overwritten locally.
Note
This example requires the
Depending on the distribution, you need a local mail transfer agent (MTA) such as Postfix, Exim or Sendmail in order to send emails.
These tools virtually provide the
mail-host-notification ¶
The mail-host-notification NotificationCommand object uses the
example notification script located in /etc/icinga2/scripts/mail-host-notification.sh.
Here is a quick overview of the arguments that can be used. See also host runtime macros for further information.
| Name | Description |
notification_date |
Required. Date and time. Defaults to $icinga.long_date_time$. |
notification_hostname |
Required. The host’s FQDN. Defaults to $host.name$. |
notification_hostdisplayname |
Required. The host’s display name. Defaults to $host.display_name$. |
notification_hostoutput |
Required. Output from host check. Defaults to $host.output$. |
notification_useremail |
Required. The notification’s recipient(s). Defaults to $user.email$. |
notification_hoststate |
Required. Current state of host. Defaults to $host.state$. |
notification_type |
Required. Type of notification. Defaults to $notification.type$. |
notification_address |
Optional. The host’s IPv4 address. Defaults to $address$. |
notification_address6 |
Optional. The host’s IPv6 address. Defaults to $address6$. |
notification_author |
Optional. Comment author. Defaults to $notification.author$. |
notification_comment |
Optional. Comment text. Defaults to $notification.comment$. |
notification_from |
Optional. Define a valid From: string (e.g. "Icinga 2 Host Monitoring <icinga@example.com>"). Requires GNU mailutils (Debian/Ubuntu) or mailx (RHEL/SUSE). |
notification_icingaweb2url |
Optional. Define URL to your Icinga Web 2 (e.g. "https://www.example.com/icingaweb2") |
notification_logtosyslog |
Optional. Set true to log notification events to syslog; useful for debugging. Defaults to false. |
mail-service-notification ¶
The mail-service-notification NotificationCommand object uses the
example notification script located in /etc/icinga2/scripts/mail-service-notification.sh.
Here is a quick overview of the arguments that can be used. See also service runtime macros for further information.
notification_date |
notification_servicename |
Required. The service name. Defaults to $service.name$. |
Required. Host display name. Defaults to $host.display_name$. |
notification_servicedisplayname |
Required. Service display name. Defaults to $service.display_name$. |
notification_serviceoutput |
Required. Output from service check. Defaults to $service.output$. |
notification_servicestate |
Required. Current state of host. Defaults to $service.state$. |
notification_type |
notification_from |
Dependencies ¶
Icinga 2 uses host and service Dependency objects for determining their network reachability.
A service can depend on a host, and vice versa. A service has an implicit dependency (parent) to its host. A host to host dependency acts implicitly as host parent relation. When dependencies are calculated, not only the immediate parent is taken into account but all parents are inherited.
The parent_host_name and parent_service_name attributes are mandatory for
service dependencies, parent_host_name is required for host dependencies.
Apply rules will allow you to
determine these attributes in a more
dynamic fashion if required.
parent_host_name = "core-router"
parent_service_name = "uplink-port"
Notifications are suppressed by default if a host or service becomes unreachable.
You can control that option by defining the disable_notifications attribute.
disable_notifications = false
If the dependency should be triggered in the parent object’s soft state, you
need to set ignore_soft_states to false.
The dependency state filter must be defined based on the parent object being
either a host (Up, Down) or a service (OK, Warning, Critical, Unknown).
The following example will make the dependency fail and trigger it if the parent object is not in one of these states:
states = [ OK, Critical, Unknown ]
In other words
If the parent service object changes into the
Warningstate, this dependency will fail and render all child objects (hosts or services) unreachable.
You can determine the child’s reachability by querying the last_reachable attribute
via the REST API.
Note
Reachability calculation depends on fresh and processed check results. If dependencies disable checks for child objects, this won’t work reliably.
Implicit Dependencies for Services on Host ¶
Icinga 2 automatically adds an implicit dependency for services on their host. That way
service notifications are suppressed when a host is DOWN or UNREACHABLE. This dependency
does not overwrite other dependencies and implicitly sets disable_notifications = true and
states = [ Up ] for all service objects.
Service checks are still executed. If you want to prevent them from happening, you can
apply the following dependency to all services setting their host as parent_host_name
and disabling the checks. assign where true matches on all Service objects.
apply Dependency "disable-host-service-checks" to Service {
disable_checks = true
assign where true
Dependencies for Network Reachability ¶
A common scenario is the Icinga 2 server behind a router. Checking internet
access by pinging the Google DNS server google-dns is a common method, but
will fail in case the dsl-router host is down. Therefore the example below
defines a host dependency which acts implicitly as parent relation too.
Furthermore the host may be reachable but ping probes are dropped by the
router’s firewall. In case the dsl-router‘s ping4 service check fails, all
further checks for the ping4 service on host google-dns service should
be suppressed. This is achieved by setting the disable_checks attribute to true.
object Host "dsl-router" {
import "generic-host"
address = "192.168.1.1"
object Host "google-dns" {
address = "8.8.8.8"
apply Service "ping4" {
import "generic-service"
check_command = "ping4"
apply Dependency "internet" to Host {
parent_host_name = "dsl-router"
assign where host.name != "dsl-router"
apply Dependency "internet" to Service {
parent_service_name = "ping4"
Apply Dependencies based on Custom Variables ¶
You can use apply rules to set parent or
child attributes, e.g. parent_host_name to other objects’
attributes.
A common example are virtual machines hosted on a master. The object name of that master is auto-generated from your CMDB or VMWare inventory into the host’s custom variables (or a generic template for your cloud).
Define your master host object:
/* your master */
object Host "master.example.com" {
Add a generic template defining all common host attributes:
/* generic template for your virtual machines */
template Host "generic-vm" {
Add a template for all hosts on your example.com cloud setting
custom variable vm_parent to master.example.com:
template Host "generic-vm-example.com" {
import "generic-vm"
vars.vm_parent = "master.example.com"
Define your guest hosts:
object Host "www.example1.com" {
import "generic-vm-master.example.com"
object Host "www.example2.com" {
Apply the host dependency to all child hosts importing the
generic-vm template and set the parent_host_name
to the previously defined custom variable host.vars.vm_parent.
apply Dependency "vm-host-to-parent-master" to Host {
parent_host_name = host.vars.vm_parent
assign where "generic-vm" in host.templates
You can extend this example, and make your services depend on the
master.example.com host too. Their local scope allows you to use
host.vars.vm_parent similar to the example above.
apply Dependency "vm-service-to-parent-master" to Service {
That way you don’t need to wait for your guest hosts becoming unreachable when the master host goes down. Instead the services will detect their reachability immediately when executing checks.
Note
This method with setting locally scoped variables only works in apply rules, but not in object definitions.
Dependencies for Agent Checks ¶
Another good example are agent based checks. You would define a health check for the agent daemon responding to your requests, and make all other services querying that daemon depend on that health check.
apply Service "agent-health" {
check_command = "cluster-zone"
display_name = "cluster-health-" + host.name
/* This follows the convention that the agent zone name is the FQDN which is the same as the host object name. */
vars.cluster_zone = host.name
assign where host.vars.agent_endpoint
Now, make all other agent based checks dependent on the OK state of the agent-health
service.
apply Dependency "agent-health-check" to Service {
parent_service_name = "agent-health"
states = [ OK ] // Fail if the parent service state switches to NOT-OK
assign where host.vars.agent_endpoint // Automatically assigns all agent endpoint checks as child services on the matched host
ignore where service.name == "agent-health" // Avoid a self reference from child to parent
This is described in detail in this chapter.
Event Commands ¶
Unlike notifications, event commands for hosts/services are called on every check execution if one of these conditions matches:
- The host/service is in a soft state
- The host/service state changes into a hard state
- The host/service state recovers from a soft or hard state to OK/Up
EventCommand objects are referenced by
with the event_command attribute.
Therefore the EventCommand object should define a command line
evaluating the current service state and other service runtime attributes
available through runtime variables. Runtime macros such as $service.state_type$
and $service.state$ will be processed by Icinga 2 and help with fine-granular
triggered events
If the host/service is located on a client as command endpoint the event command will be executed on the client itself (similar to the check command).
Common use case scenarios are a failing HTTP check which requires an immediate restart via event command. Another example would be an application that is not responding and therefore requires a restart. You can also use event handlers to forward more details on state changes and events than the typical notification alerts provide.
Use Event Commands to Send Information from the Master ¶
This example sends a web request from the master node to an external tool
for every event triggered on a businessprocess service.
Define an EventCommand
object send_to_businesstool which sends state changes to the external tool.
object EventCommand "send_to_businesstool" {
command = [
"/usr/bin/curl",
"-s",
"-X PUT"
arguments = {
"-H" = {
value ="$businesstool_url$"
skip_key = true
"-d" = "$businesstool_message$"
vars.businesstool_url = "http://localhost:8080/businesstool"
vars.businesstool_message = "$host.name$ $service.name$ $service.state$ $service.state_type$ $service.check_attempt$"
Set the event_command attribute to send_to_businesstool on the Service.
object Service "businessprocess" {
host_name = "businessprocess"
check_command = "icingacli-businessprocess"
vars.icingacli_businessprocess_process = "icinga"
vars.icingacli_businessprocess_config = "training"
event_command = "send_to_businesstool"
In order to test this scenario you can run:
nc -l 8080
This allows to catch the web request. You can also enable the debug log and search for the event command execution log message.
tail -f /var/log/icinga2/debug.log | grep EventCommand
Feed in a check result via REST API action process-check-result or via Icinga Web 2.
Expected Result:
# nc -l 8080
PUT /businesstool HTTP/1.1
User-Agent: curl/7.29.0
Host: localhost:8080
Accept: */*
Content-Length: 47
Content-Type: application/x-www-form-urlencoded
businessprocess businessprocess CRITICAL SOFT 1
Use Event Commands to Restart Service Daemon via Command Endpoint on Linux ¶
This example triggers a restart of the httpd service on the local system
when the procs service check executed via Command Endpoint fails. It only
triggers if the service state is Critical and attempts to restart the
service before a notification is sent.
Requirements:
- Icinga 2 as client on the remote node
- icinga user with sudo permissions to the httpd daemon
Example on CentOS 7:
# visudo
icinga ALL=(ALL) NOPASSWD: /usr/bin/systemctl restart httpd
Note: Distributions might use a different name. On Debian/Ubuntu the service is called apache2.
Define an EventCommand object restart_service
which allows to trigger local service restarts. Put it into a global zone
to sync its configuration to all clients.
[root@icinga2-master1.localdomain /]# vim /etc/icinga2/zones.d/global-templates/eventcommands.conf
object EventCommand "restart_service" {
command = [ PluginDir + "/restart_service" ]
arguments = {
"-s" = "$service.state$"
"-t" = "$service.state_type$"
"-a" = "$service.check_attempt$"
"-S" = "$restart_service$"
vars.restart_service = "$procs_command$"
This event command triggers the following script which restarts the service.
The script only is executed if the service state is CRITICAL. Warning and Unknown states
are ignored as they indicate not an immediate failure.
[root@icinga2-agent1.localdomain /]# vim /usr/lib64/nagios/plugins/restart_service
#!/bin/bash
while getopts "s:t:a:S:" opt; do
case $opt in
s)
servicestate=$OPTARG
t)
servicestatetype=$OPTARG
a)
serviceattempt=$OPTARG
S)
service=$OPTARG
esac
done
if ( [ -z $servicestate ] || [ -z $servicestatetype ] || [ -z $serviceattempt ] || [ -z $service ] ); then
echo "USAGE: $0 -s servicestate -z servicestatetype -a serviceattempt -S service"
exit 3;
else
# Only restart on the third attempt of a critical event
if ( [ $servicestate == "CRITICAL" ] && [ $servicestatetype == "SOFT" ] && [ $serviceattempt -eq 3 ] ); then
sudo /usr/bin/systemctl restart $service
fi
fi
[root@icinga2-agent1.localdomain /]# chmod +x /usr/lib64/nagios/plugins/restart_service
Add a service on the master node which is executed via command endpoint on the client.
Set the event_command attribute to restart_service, the name of the previously defined
EventCommand object.
[root@icinga2-master1.localdomain /]# vim /etc/icinga2/zones.d/master/icinga2-agent1.localdomain.conf
object Service "Process httpd" {
check_command = "procs"
event_command = "restart_service"
max_check_attempts = 4
command_endpoint = "icinga2-agent1.localdomain"
vars.procs_command = "httpd"
vars.procs_warning = "1:10"
vars.procs_critical = "1:"
In order to test this configuration just stop the httpd on the remote host icinga2-agent1.localdomain.
[root@icinga2-agent1.localdomain /]# systemctl stop httpd
You can enable the debug log and search for the executed command line.
[root@icinga2-agent1.localdomain /]# tail -f /var/log/icinga2/debug.log | grep restart_service
Use Event Commands to Restart Service Daemon via Command Endpoint on Windows ¶
This example triggers a restart of the httpd service on the remote system
when the service-windows service check executed via Command Endpoint fails.
It only triggers if the service state is Critical and attempts to restart the
Requirements:
- Icinga 2 service with permissions to execute Powershell scripts (which is the default)
Define an EventCommand object restart_service-windows
object EventCommand "restart_service-windows" {
command = [
"C:\\Windows\\SysWOW64\\WindowsPowerShell\\v1.0\\powershell.exe",
PluginDir + "/restart_service.ps1"
arguments = {
"-ServiceState" = "$service.state$"
"-ServiceStateType" = "$service.state_type$"
"-ServiceAttempt" = "$service.check_attempt$"
"-Service" = "$restart_service$"
"; exit" = {
order = 99
value = "$$LASTEXITCODE"
vars.restart_service = "$service_win_service$"
Add the restart_service.ps1 Powershell script into C:\Program Files\Icinga2\sbin:
param(
[string]$Service = '',
[string]$ServiceState = '',
[string]$ServiceStateType = '',
[int]$ServiceAttempt = ''
if (!$Service -Or !$ServiceState -Or !$ServiceStateType -Or !$ServiceAttempt) {
$scriptName = GCI $MyInvocation.PSCommandPath | Select -Expand Name;
Write-Host "USAGE: $scriptName -ServiceState servicestate -ServiceStateType servicestatetype -ServiceAttempt serviceattempt -Service service" -ForegroundColor red;
exit 3;
if ($ServiceState -eq "CRITICAL" -And $ServiceStateType -eq "SOFT" -And $ServiceAttempt -eq 3) {
Restart-Service $Service;
exit 0;
Set the event_command attribute to restart_service-windows, the name of the previously defined
[root@icinga2-master1.localdomain /]# vim /etc/icinga2/zones.d/master/icinga2-agent2.localdomain.conf
object Service "Service httpd" {
check_command = "service-windows"
event_command = "restart_service-windows"
host_name = "icinga2-agent2.localdomain"
command_endpoint = "icinga2-agent2.localdomain"
vars.service_win_service = "httpd"
C:> net stop httpd
executed command line in C:\ProgramData\icinga2\var\log\icinga2\debug.log.
Use Event Commands to Restart Service Daemon via SSH ¶
This example triggers a restart of the httpd daemon
via SSH when the http service check fails.
Requirements:
- SSH connection allowed (firewall, packet filters)
- icinga user with public key authentication
- icinga user with sudo permissions to restart the httpd daemon.
Example on Debian:
# ls /home/icinga/.ssh/
authorized_keys
# visudo
icinga ALL=(ALL) NOPASSWD: /etc/init.d/apache2 restart
Define a generic EventCommand object event_by_ssh
which can be used for all event commands triggered using SSH:
[root@icinga2-master1.localdomain /]# vim /etc/icinga2/zones.d/master/local_eventcommands.conf
/* pass event commands through ssh */
object EventCommand "event_by_ssh" {
command = [ PluginDir + "/check_by_ssh" ]
arguments = {
"-H" = "$event_by_ssh_address$"
"-p" = "$event_by_ssh_port$"
"-C" = "$event_by_ssh_command$"
"-l" = "$event_by_ssh_logname$"
"-i" = "$event_by_ssh_identity$"
"-q" = {
set_if = "$event_by_ssh_quiet$"
"-w" = "$event_by_ssh_warn$"
"-c" = "$event_by_ssh_crit$"
"-t" = "$event_by_ssh_timeout$"
vars.event_by_ssh_address = "$address$"
vars.event_by_ssh_quiet = false
The actual event command only passes the event_by_ssh_command attribute.
The event_by_ssh_service custom variable takes care of passing the correct
daemon name, while test $service.state_id$ -gt 0 makes sure that the daemon
is only restarted when the service is not in an OK state.
object EventCommand "event_by_ssh_restart_service" {
import "event_by_ssh"
//only restart the daemon if state > 0 (not-ok)
//requires sudo permissions for the icinga user
vars.event_by_ssh_command = "test $service.state_id$ -gt 0 && sudo systemctl restart $event_by_ssh_service$"
Now set the event_command attribute to event_by_ssh_restart_service and tell it
which service should be restarted using the event_by_ssh_service attribute.
check_command = "http"
event_command = "event_by_ssh_restart_service"
vars.event_by_ssh_service = "$host.vars.httpd_name$"
//vars.event_by_ssh_logname = "icinga"
//vars.event_by_ssh_identity = "/home/icinga/.ssh/id_rsa.pub"
assign where host.vars.httpd_name
Specify the httpd_name custom variable on the host to assign the
service and set the event handler service.
object Host "remote-http-host" {
address = "192.168.1.100"
vars.httpd_name = "apache2"
[root@icinga2-agent1.localdomain /]# tail -f /var/log/icinga2/debug.log | grep by_ssh